I am installing a tap (25' or less). The existing feeder is 480V and protected by 800 Amp fuses. The new feeder tap is called to be 4-600kCMil + 1/0 gnd and feeds a 400 amp main breaker in a new sub panel. The sub panel only has 3 phase loads ( (2) 90 Amp Air Handlers, (2) 125 Amp Condensers, and (2) 15 Amp Gas Heat), but room for someone down the road to install more loads.
I think there is a problem: am I supposed use Table 310.15(B)(2)(a) Adjustment Factors for More Than Three Current-Carrying Conductors in a Raceway? 3 phases and 1 neutral. So 80%. 600s are 475 Amp *80% = 380. So this is less than the 400 Amps.
I was going to suggest to use 2 sets of (3) 3/0 + 1/0 gnd.
But if they want the neutral, do I need to put 2 sets of (4) 4/0 + 1/0 gnd. 2 * 260 Amps * 80% = 416 Amps.
I believe each of these would also satisfy the 25' tap rules.
I think there is a problem: am I supposed use Table 310.15(B)(2)(a) Adjustment Factors for More Than Three Current-Carrying Conductors in a Raceway? 3 phases and 1 neutral. So 80%. 600s are 475 Amp *80% = 380. So this is less than the 400 Amps.
I was going to suggest to use 2 sets of (3) 3/0 + 1/0 gnd.
But if they want the neutral, do I need to put 2 sets of (4) 4/0 + 1/0 gnd. 2 * 260 Amps * 80% = 416 Amps.
I believe each of these would also satisfy the 25' tap rules.