25 ft Transformer Secondary Conductors

Status
Not open for further replies.
As I understand things from the NEC:
240.21(C)(3) - For industrial installations, you do not need overcurrent protection at the transformer if your secondary conductors are not over 25 ft, the conductors can carry the full load current of the transformer, and the sum of over current devices does not exceed the ampacity of the secondary conductors.

240.21(C)(6) - For other installations, you can use conductors not over 25 ft that terminate in a single set of fuses. These conductors must be at least 1/3 of the primary overcurrent device referred to the secondary side.

As far as I can tell, the advantage of 240.21(C)(3) is that you can have multiple sets of fuses. 240.21(C)(6) only lets you use one set.

My question:
Do I have to use 240.21(C)(3) for any industrial installation or can I use 240.21(C)(6)?
 
240.21(C)(3) is for industrial installations only.

240.21(C)(6) could be used in an industrial setting as well.

Pete
 
As far as I can tell, the advantage of 240.21(C)(3) is that you can have multiple sets of fuses. 240.21(C)(6) only lets you use one set.

I agree with Pete.

I don't, however, see the advantage that you mention above.

I think a better way to read the difference between 240.21(C)(3) and (C)(6) is that:

240.21(C)(3) allows multiple sets of fuses for one set of transformer secondary conductors, while 240.21(C)(6) allows one set of fuses for multiple sets of transformer secondary conductors.
 