I was wondering if you guys see anything wrong for to use a a 25 kV fuse on 15 kV line? it does not seems to be a mistake? Any idea?
The 25 kV fuse might require a longer cutout. Depends.
However, using a higher kV fuse on a lower kV system will change the melting characteristics. Think of the fuse as a resistor. The link is melted by applying adequate energy during an overcurrent.
More energy is required to melt a higher voltage fuse so it should react slower than expected.
Generally fuses don't work that way. They generate heat from the current flowing through them (I^2R). Voltage level does not make a lot of difference. It is like a resistor but the amount of heat is strictly a function of I^2R. note V is not in the equation.
It is possible that the TCC characteristics for 15KV fuses are different from 25KV fuses.
Generally fuses don't work that way. They generate heat from the current flowing through them (I^2R). Voltage level does not make a lot of difference. It is like a resistor but the amount of heat is strictly a function of I^2R. note V is not in the equation.
It is possible that the TCC characteristics for 15KV fuses are different from 25KV fuses.
Look at a 10A 120 volt fuse and a 10A 69 kV fuse. A bit extreme but you get the idea. The characteristics will vary.Generally fuses don't work that way. They generate heat from the current flowing through them (I^2R). Voltage level does not make a lot of difference. It is like a resistor but the amount of heat is strictly a function of I^2R. note V is not in the equation.
It is possible that the TCC characteristics for 15KV fuses are different from 25KV fuses.
It seems that using a higher voltage rated fuse may not be as big of a deal with expulsion fuses but it does seem to be a problem with current-limiting fuses because of the higher arc voltage and equipment BIL rating.Look at a 10A 120 volt fuse and a 10A 69 kV fuse. A bit extreme but you get the idea. The characteristics will vary.
The difference between a 25 kV recloser curve and a 15 kV recloser curve is not much so there may not be a lot of difference in a 12 kV fuse and 25 kV fuse. I have substituted reclosers.
I have never switched fuses as I was always able to get the correct one whenever needed. Common stock item.
Add: also think about the arcing for an expulsion fuse. The arcing produces the gases needed to blow out the arc. The arc disintegrates the inside of the barrel to produce the gas needed. 25 kV will not arc the same as 12 kV.
I was thinking along the same lines as you here, and I don't really know that voltage rating has too much to do with trip curves, they mostly should respond to current.Generally fuses don't work that way. They generate heat from the current flowing through them (I^2R). Voltage level does not make a lot of difference. It is like a resistor but the amount of heat is strictly a function of I^2R. note V is not in the equation.
It is possible that the TCC characteristics for 15KV fuses are different from 25KV fuses.
Been a while, but as I recall, a recloser (and it's associated bushings) rated 7,200/12,470 is nameplate rated 15KV and a 14,400/24,940 is rated 25KV. Their ratings were based on line to line, not line to neutral, even if it was a single phase line to neutral recloser. If it was used on a 7,200 recloser, it was rated 15KV. Not sure why. I think fuses were the same, but I'm not sure. Been retired too long.![]()
But don't those voltage ratings have more to do with insulation rating and "open circuit" ratings more so then actual trip curves?
A 25kV switch shouldn't be a problem with any kind of flashing across open contact if only 15kV is what is being supplied, but the other way around could be a problem.
Yet a 10 amp fuse should have same trip curve on either voltage, it just needs to have proper voltage rating for safely interrupting same level of current, as well as interrupt ratings that are high enough for available fault current.
But at same time 4 the current is more of an overload condition and not a short circuit/ground fault condition, so you get a delay action on lower level of overcurrent then you do with the rapid rise in current that happens in short circuits/ground faults.Sounds reasonable regarding a switch, but I'm no protection engineer. It could be that an expulsion fuse requires a certain amount of "power" to clear a fault properly. Since a fuse is basically a resistor, using a fuse at half of the voltage rating would require 4X the "current" to produce the same power available at the fuse during a fault. P=E sq/R Ohm's Law, not mine..... Could be that a lower than rated voltage would allow a longer duration arc, negatively affecting the trip time, especially on an expulsion fuse. I really have no idea, but I wanted to sound "Ejukated!):dunce:
That's true enough for some. They can fit a wide range of voltages. But if there is a catalog of voltages, they are specific for a reason. I just read that was important for current limiting fuses.I was thinking along the same lines as you here, and I don't really know that voltage rating has too much to do with trip curves, they mostly should respond to current.
Perhaps it matters due to the arc it has to create and how it extinguishes the arc. The length of the element, the element shape/size/configuration and difference for different voltages may play a role.Sure more voltage on same circuit may possibly result in more current (and more power) being pumped into a fault - but how much current can flow is also dependent on impedance of the source and supply conductors just like it is for lower voltages isn't it?
Practically none before it is damaged. But when it starts to heat then melt it certainly rises.How much volts drops across a fuse when operating volts is in the 15kV+ range?
But it could be the operating mechanism or protected system is sensitive somehow. Certainly seems to be the case for current limiting fuses anyway.I am not a MV guy, but Ohm's law doesn't change just because the voltage is significantly higher either.
Look at a 10A 120 volt fuse and a 10A 69 kV fuse. A bit extreme but you get the idea. The characteristics will vary.
The difference between a 25 kV recloser curve and a 15 kV recloser curve is not much so there may not be a lot of difference in a 12 kV fuse and 25 kV fuse. I have substituted reclosers.
I have never switched fuses as I was always able to get the correct one whenever needed. Common stock item.
Add: also think about the arcing for an expulsion fuse. The arcing produces the gases needed to blow out the arc. The arc disintegrates the inside of the barrel to produce the gas needed. 25 kV will not arc the same as 12 kV.
Some fuses are multi-voltage, some are more limited.Been a while, but as I recall, a recloser (and it's associated bushings) used on 7,200/12,470 is nameplate rated 15KV and a 14,400/24,940 is rated 25KV. Their ratings were based on line to line, not line to neutral, even if it was a single phase line to neutral recloser. If it was used on a 7,200 single phase circuit, it was rated 15KV. Not sure why. I think fuses were the same, but I'm not sure. Been retired too long.![]()
Our line fuses covered from 2.4 kV to 35 kV systems.You are right- but you've never applied a 15kv fuse to a 4.16kv system or a 25kv fuse to a 12kv system because the voltage will latter be increased? Very common for POCO working on abandoning legacy systems.
Been a while, but as I recall, a recloser (and it's associated bushings) used on 7,200/12,470 is nameplate rated 15KV and a 14,400/24,940 is rated 25KV. Their ratings were based on line to line, not line to neutral, even if it was a single phase line to neutral recloser. If it was used on a 7,200 single phase circuit, it was rated 15KV. Not sure why. I think fuses were the same, but I'm not sure. Been retired too long.![]()
Our line fuses covered from 2.4 kV to 35 kV systems.