Most of the time when I see a 25kva electric furnace it usually will have 3 branch circuits- (2) 60-amp & (1) 30-amp circuits.
This setup is comprised of (2) 10 kva & (1) 5 kva heating elements setup to make a total of 25 kva.
In the last year I’ve seen 2 furnaces of this size that were set up with (2) branch circuits- (1) 15 kva & (1) 10 kva. This requires (1) 80-amp circuit (4-awg) & (1) 60-amp circuit (6-awg).
In my opinion, regarding the electrical requirements and installation for this new furnace, this is a royal PITA! 4-awg THHN is expensive!
Is there any specific reason that the 2 branch circuit setup is being used over the 3 branch circuit furnace?
Both furnaces that I encountered were update/retrofit furnaces that were using this new furnace to replace an existing furnace, so there was already the proper wiring there for the 3 branch circuit furnace, but now I have to try and retro-install 4-awg wire to feed the 15-kva circuit!
This setup is comprised of (2) 10 kva & (1) 5 kva heating elements setup to make a total of 25 kva.
In the last year I’ve seen 2 furnaces of this size that were set up with (2) branch circuits- (1) 15 kva & (1) 10 kva. This requires (1) 80-amp circuit (4-awg) & (1) 60-amp circuit (6-awg).
In my opinion, regarding the electrical requirements and installation for this new furnace, this is a royal PITA! 4-awg THHN is expensive!
Is there any specific reason that the 2 branch circuit setup is being used over the 3 branch circuit furnace?
Both furnaces that I encountered were update/retrofit furnaces that were using this new furnace to replace an existing furnace, so there was already the proper wiring there for the 3 branch circuit furnace, but now I have to try and retro-install 4-awg wire to feed the 15-kva circuit!