Clamp on ground readings
Clamp on ground readings
Before everyone gets on my case, here is why:
1. How it works: It sets up a current in the ground circuit by magnetic induction. It then measures the current and voltage drop to determine the resistance. Ideally the ground being measured is a ground rod in a system of many other ground rods.
2. Pitfalls and Tips: Like any other instrument it has limitations. Please read the manual. There are a few real important items to notice like...
a. There MUST BE AT LEAST TWO EARTH GROUNDS (ground rods) in the ground circuit for it to work properly. If you try to measure one ground rod, it will read OL (out of range). The meter's limit is 1200 OHMS, after that it will read OL. OL means that the ground circuit is open or the ground resistance is over 1200 ohms. A tactical ground should be far less than 1200 ohms, more like 25 ohms.
b. Also, the fewer ground rods in the circuit, the less accurate it is. This is because a clamp on ground tester uses other ground rods in the system (added in parallel) as a reference. If there are only two ground rods, the reading you are getting is the SUM of the two resistances. It is not possible to tell (with this instrument) if one ground rod has a greater resistance than the other when there are only two ground rods in the circuit.
c. There is a warning on the meter that reads R<1 OHM. If this is on, the reading is inaccurate and you are measuring a closed circuit conductive loop.
d. There is a warning on the meter that reads "NOISE". If this is on, there is over 50V or over 5A on the ground circuit. There is probably an electrical fault condition if this is true - power down the system and render it safe until the problem can be corrected.
e. Another pitfall is that the conductive contacts in the jaws get dirty. Wipe them frequently with a SOFT lint-free cloth. If the contacts are dirty, the meter will indicate "jaws open" or possibly read OL.