bobby ocampo
Senior Member
What is the basis of the Code for the 25 ohms requirement?
What is the basis of the Code for the 25 ohms requirement?
No one seems to know with any degree of certainty.
I have seen some speculation that it may be based on telegraph specs that only had one wire and used the earth as the second conductor so a decent connection to the earth was required.
Old habits die hard and slow.What is the basis of the Code for the 25 ohms requirement?
What is the basis of the Code for the 25 ohms requirement?
Back in the very early days about all telephone circuits were Party Lines. Remember those? Anyway in those days Ring Voltage was applied between to the either Tip or Ring conductor and Earth. Thus the telephone office had to have a low resistance to earth. This allowed the telco to run 9 circuits on a single line and the ability to ring a one specific phone shared with 8 others.
No real reason to make it higher or lower as it does not have much of a function. If anything an upper limit like 500 Ohm's which is about what you get out of an average ground rod. Anything 500 or less with the current requirements is adequate.Any information if the Code or the IEEE have done research as to the validity of this 25 ohm requirement? Is 25 ohm safe? Is it recommended for residential only?
If the ground resistance should be as low as practically as possible, why 25 ohms? Have somebody recommended to make it lower or higher in the Code revision?
No real reason to make it higher or lower as it does not have much of a function. If anything an upper limit like 500 Ohm's which is about what you get out of an average ground rod. Anything 500 or less with the current requirements is adequate.
If you get it to low say less than 1 then you actually make safety and operational problems as significant current will be flowing through earth and if you were to loose your service grounded conductor may go undetected like in the ole days when when water pipes were metallic and water departments did not install isolation bushings in water meters.
However there is no need to change the 25 ohm requirement because it is meaningless paper tiger. Bond the water pipe, rebar if available, drive two grounds rods and call it done. It could be 5000 or 5 ohms and it complies.
The code doesn't really require a ground resistance of 25 ohms or less. It just says that if a singe driven rod or pipe or a buried plate type electrode has a resistance greater than 25 ohms that you have to provide a second electrode.If it is meaningless then why require 25 ohm? Why not 500 ohms as you said?
What do you mean sir of loosing the service grounded conductor? Is this the neutral?
As I said old habits die hard and hard to break. It is old language based on antiquated technology. As Don stated there is no requirement to achieve 25 ohm. All you have to do is drive two ground rods, collect a check, and call it a day.If it is meaningless then why require 25 ohm? Why not 500 ohms as you said?
Correct. But I left out a word in my haste: Grounded Circuit ConductorWhat do you mean sir of loosing the service grounded conductor? Is this the neutral?
I thought it came from trying to get a value lower than that of the human body, which comes in around 300-1,000 ohms. In that respect, shooting for 25 leaves a bit of wiggle room.
Why would that make any difference?I thought it came from trying to get a value lower than that of the human body, which comes in around 300-1,000 ohms. In that respect, shooting for 25 leaves a bit of wiggle room.
answer is simple, there was a survey in U.S. to know the average of the resistance with the water pipes available in the country, 25 ohms was resistance measurement that was feasible for most of the services in the country
As I said old habits die hard and hard to break. It is old language based on antiquated technology. As Don stated there is no requirement to achieve 25 ohm. All you have to do is drive two ground rods, collect a check, and call it a day.
It would be really difficult for most EC's to prove 25 ohms or less on a single rod as most do not have the equipment, nor the time and training to perform valid test and in most cases impossible to get valid test. Much easier, less time, and less expense to just drive two rods and call it done. To perform a Dead Fall Potential Test can take all day and most of the readings would be invalid and meaningless in an urban environment. It is just simple economics and good biz to just drive two rods to comply.