25-ohms ??

Merry Christmas
Status
Not open for further replies.

tpwd

Member
Location
Texas
the NEC does not refer to 25-ohms resistance to grounding except on a "driven" ground rod. it says that if one rod does not meet this, you must used another grounding method [which can be another rod]...no where does it require any value of resistance after you install another one. what does your inspectors require? most likely what ever they dream up. can anyone reference a value?...thanks :confused:
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: 25-ohms ??

This is the reason the GEC to a rod or rods does not need to be more than a #6 copper. In otherwords the average ground rod or rods aren't good for much in everyday faults at nominal voltages. (Placebos)

They do come to play in high surges or lightning strikes, and at these elevated voltages they would disperse some of the fault.

Roger

[ April 07, 2003, 06:17 PM: Message edited by: roger ]
 

bennie

Esteemed Member
Re: 25-ohms ??

The April 2000 issue of EC&M Magazine has a good article... Who cares about 25 ohms or less?.
 

wocolt

Member
Location
Ohio
Re: 25-ohms ??

In my area the rule of thumb is, show me 25 ohms to ground or drive two ground rods. Obviously not many of us have a tester, so we drive two ground rods; Also we have to leave a mound of dirt at each rod so the inspector can verify that they actually do exist that is the rods are subsurface but easy enough for him to kick the dirt into the hole after verification.
One ground rod here wont get it, but gets the red-tag if only one is driven.

WOC
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: 25-ohms ??

Hey Bennie and William. William, our AHJ's require the same thing unless we show them, and we do have testers. The problem is, any given day the soil conditions are different and we even have clay. So we drive two rods and go on. :)

Roger
 

eprice

Senior Member
Location
Utah
Re: 25-ohms ??

I pretty much agree with the answers that have been given. however, I would point out that the 25 ohm rule (250.56) applies to pipe and plate electrodes as well. I have never seen either of these two types used and if I ever do, hopefully I will be able to remind my self that there will need to be two unless 25 ohms or less has been met.

Does anyone have any particular thoughts on why plate electrodes are not used more often, particularly in areas where driving rods is difficult because of rock near the surface? Is it just because no one thinks about them or because the local electrical supply doesn't stock them?
 

tpwd

Member
Location
Texas
Re: 25-ohms ??

thank you all for replying...we inspectors require the resistance to be 25-ohms or less no matter what you use to get there. we use an AEMC clamp-on ground resistance tester to verify this. we only accept ground rods as the last resort to ground a service. i have been asking this question for many years....no one [especially NEC code writers] will answer it. they all say the "authority having jurisdiction" [which is a phrase used to pass-the-buck] shall make the call.
if this is a safety issue, why don't we put a value on it?...if not why drive another rod if it doesn't work anyway???....thanks to all
 

bennie

Esteemed Member
Re: 25-ohms ??

The connection to earth is not a safety factor. Transients produced by lightning don't care if it is 25 or 125.

The equipment ground conductor system is important and should be circuited as carefully as the active line side. Design should not allow normal mode current or common mode current to flow.
 

bennie

Esteemed Member
Re: 25-ohms ??

eprice: The only ground plates, I have installed, are pole butt plates, on distribution secondary racks.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: 25-ohms ??

tpwd,
we inspectors require the resistance to be 25-ohms or less no matter what you use to get there
Do you mean that you are requiring additional grounding electrodes until the resistance is 25 ohms?
Don
 

bennie

Esteemed Member
Re: 25-ohms ??

Good point Don, I know of places, in the world, where 25 ohms can never be obtained regardless of number of rods.
 

wocolt

Member
Location
Ohio
Re: 25-ohms ??

Bennie
you are right, lightning doesnt care if it hits the service mast or the tree standing next to the house.
That said, it still is a level of safty better than no ground rod(s) at all.

WOC
 

tpwd

Member
Location
Texas
Re: 25-ohms ??

yes...all the electrical engineers that i have talked with [over 25] say they want 25-ohms or less on services?....so we enforce them...i don't know where you can't get the resistance under 25-ohms if you try, we install services in granite outcropping area and have to use a engineered design, sometimes beninite composite...but usely burying 20' of #2 copper gets the resistance down..
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: 25-ohms ??

Tpwd, in your oppinion, what is their reason for wanting this, besides the NEC standard?

Roger
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: 25-ohms ??

tpwd,
An inspector can only enforce the code, he has no business enforcing design specs. The design specs are to be enforced by the owner or his representee. The code does not require you to add additional grounding electrodes to get the system down to 25 ohms.
Don
 

hurk27

Senior Member
Re: 25-ohms ??

the whole idea of 25 ohm's is just a reference point as if the ground rod cant get below that then the code only requires that you install one additional ground rod and after that there is no more requirement for the 25 ohm's.
The reason for this is simple if the ground is at that high of resistance then it probably will not matter how good of ground you get because the lightning will probably not hit the EGC system anyway and just go around it as it does not care if your connected to the electrical grid or not as it only wants to get to the earth (it's opposite pole) and will go through anything to get there. the resistance of a ground is just a reference point of how resistive the earth is at the point of connection. and will not protect you any better from a lightning strike. with this said then we can say that if a ground rod has 50 ohms on it and adding another one only brings it down to 45 ohms then adding more will not add to any protection in any way. and might even cause you to have more direct strikes as you will be like a brighter light in a dark room to the lightning and will attract more strikes in stead of just hitting the ground or a tree down the road or somewhere the ground does have a lower resistance. and since no grounding can protect 100% against a damage from a lighting strike then it would be better that it hit down the road than hit your house as it destroys most things that it hits.
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: 25-ohms ??

Don you hit the nail on the head. Unless there is a local code requirement for 25 or less, a local inspector has no buisness trying to enforce a design spec. There is nowhere in the NEC that states the ground resistance shall be 25 or less.
 

hornetd

Senior Member
Location
Maryland
Occupation
Journeyman Electrician, Retired
Re: 25-ohms ??

Originally posted by tpwd:
posted April 08, 2003 12:36 PM thank you all for replying...we inspectors require the resistance to be 25 ohms or less no matter what you use to get there. we use an AEMC clamp-on ground resistance tester to verify this. we only accept ground rods as the last resort to ground a service. i have been asking this question for many years....no one [especially NEC code writers] will answer it. they all say the "authority having jurisdiction" [which is a phrase used to pass-the-buck] shall make the call.
if this is a safety issue, why don't we put a value on it?...if not why drive another rod if it doesn't work anyway???....thanks to all
He then added the following.

yes...all the electrical engineers that i have talked with [over 25] say they want 25-ohms or less on services?....so we enforce them...i don't know where you can't get the resistance under 25-ohms if you try, we install services in granite outcropping area and have to use a engineered design, sometimes beninite composite...but usually burying 20' of #2 copper gets the resistance down..
Long time participants here already know that inspectors who make up rules as they go along are a very sore subject with me. So they can go on to another post. For those not familiar with the legal implications of inspector conduct I offer the following.

Let me express the hope that you are either a contract compliance inspector, rather than a public agency AHJ, or that you have a locally adopted code or amendment to provide legal authority for your position. If you are ordering contractors to meet this twenty five ohm bench mark without contract or statutory authority you are engaged in the essence of arbitrary and capricious abuse of office. If your state has a state wide board of appeals a review of there decisions will reveal that if the requirement is not in a code that is adopted pursuant to statute then the inspector can only order a change based on the legal doctrine of clear and present danger. That means that if you have no code provision that requires the change you have to show that the present condition is an immediate danger to public safety. The reason that the US NEC does not require that the grounding electrode system meet a specific ground impedance value that there is no scientific or experiential basis for such a standard.

I am willing to concede that most such "field expedient corrections," on the part of public agency AHJs, are ordered in good faith by conscientious men and women who are just trying to do a good job. The problem is that such conduct reveals that the public agency that employs you has failed to provide adequate training in the application of administrative law. To tolerate public officials making up rules that they then enforce as law is to set up little tin pot gods that are acting outside the law. Such conduct will inevitably bring the entire code enforcement process into public disrepute. This is not intended as a personal attack on you but rather a statement of my belief that the enforcement of the code AS WRITTEN is the key to public acceptance and confidence in the regulatory process.
--