When dealing with something as common as a residential water heater, there can be some confusion as to how much overcurrent protection is needed.
Case in point: Take your standard 4500 watt electric water heater. Operating at 240 Volts, it requires 18.75 Amps. On the surface, that would appear to require a 20 amp circuit. But wait!! Doesn't the Code require a continuous load to be figured at 125% capacity when determining feeder and branch circuit sizing? That translates into 23.44 Amps, more than your typical 20 Amp circuit can supply.
Mobile and modular home manufacturers have responded by installing 25 Amp breakers in their panels to satisfy this load and requirement.
For years, I've always used a 30 Amp circuit with a #10 AWG wire for such a load. It's just the way we have always done it one might assume.
But am I required to use a 25 Amp breaker? Or does it not make any difference if I choose to install a 30 instead?
Case in point: Take your standard 4500 watt electric water heater. Operating at 240 Volts, it requires 18.75 Amps. On the surface, that would appear to require a 20 amp circuit. But wait!! Doesn't the Code require a continuous load to be figured at 125% capacity when determining feeder and branch circuit sizing? That translates into 23.44 Amps, more than your typical 20 Amp circuit can supply.
Mobile and modular home manufacturers have responded by installing 25 Amp breakers in their panels to satisfy this load and requirement.
For years, I've always used a 30 Amp circuit with a #10 AWG wire for such a load. It's just the way we have always done it one might assume.
But am I required to use a 25 Amp breaker? Or does it not make any difference if I choose to install a 30 instead?