For a fun-filled Friday afternoon, i have just been informed that my very carefully measured (on paper :roll: ) 25' tap will likely end up being 26-27' long and the inspector didn't go for it. nothing can change location, so I'm looking for options.
a little background: we are replacing a 2000A MCC and adding a separate 1000A MCC to a plant. Both will be fed from a 3000A breaker on the secondary of the plant transformer. the feeder to the 2000A MCC would not be considered a tap becasue it is rated at the full 3000A. Each one has a main breaker. we need to keep them separately isolatable because the 1000A one will be supporting necessary plant functions while we rip out and replace the old 2000A one.
i have a suggestion that we put another breaker/fused switch in between the main breaker and the new 1000A MCC. It seems like it will satisfy code but look like a kluge and cost more than I would like.
I'm up for any expert opinions you care to offer (and one or three beers)
thanks,
a little background: we are replacing a 2000A MCC and adding a separate 1000A MCC to a plant. Both will be fed from a 3000A breaker on the secondary of the plant transformer. the feeder to the 2000A MCC would not be considered a tap becasue it is rated at the full 3000A. Each one has a main breaker. we need to keep them separately isolatable because the 1000A one will be supporting necessary plant functions while we rip out and replace the old 2000A one.
i have a suggestion that we put another breaker/fused switch in between the main breaker and the new 1000A MCC. It seems like it will satisfy code but look like a kluge and cost more than I would like.
I'm up for any expert opinions you care to offer (and one or three beers)