250.102 (C) (1) Table Q

Status
Not open for further replies.

zcanyonboltz

Senior Member
Location
denver
250.102 (C) (1) is used to size bonding jumpers, I don't understand why the table says Grounded Conductor? I thought grounded conductor was sized using 220.61 and by doing calculations based on article 220? Thanks
 
We used to use table 250.66. CMPs felt the need to copy and paste that table into 250.102.

Somebody needs to find these guys something to do where they can all sit around and still feel important.
Having the additional table gets rid of the problems with changes you had to make to T250.66 where you were using that table for something other than sizing the GEC.
 