Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
The engineering firm has undersized the supply side bonding jumper from the transformer secondary to the Swgr CB. Can engineering calculations suffice per NEC 240 versus performing a lot of rework?

They’re running 500kCMIL, 13 per phase in multiple 4” underground PVC conduits and each conduit has a #2/0 bonding jumper...BUT according to 250.102(C)(1) it should be 12.5% of the total kCMIL area i.e. 13x500kCMILx.125=812kCMIL


Sent from my iPhone using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
For SSBJ see 250.012(C)(2).
With parallel conduits you can base the size on the conductors in each conduit.
Your MBJ would be based ion the 12-1/2%
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
For copper 500 kcmil only a #1/0 is required in each raceway.
 