Isaiah
Senior Member
- Location
- Baton Rouge
- Occupation
- Electrical Inspector
The engineering firm has undersized the supply side bonding jumper from the transformer secondary to the Swgr CB. Can engineering calculations suffice per NEC 240 versus performing a lot of rework?
They’re running 500kCMIL, 13 per phase in multiple 4” underground PVC conduits and each conduit has a #2/0 bonding jumper...BUT according to 250.102(C)(1) it should be 12.5% of the total kCMIL area i.e. 13x500kCMILx.125=812kCMIL
Sent from my iPhone using Tapatalk
They’re running 500kCMIL, 13 per phase in multiple 4” underground PVC conduits and each conduit has a #2/0 bonding jumper...BUT according to 250.102(C)(1) it should be 12.5% of the total kCMIL area i.e. 13x500kCMILx.125=812kCMIL