300.3(B) Conductors of the Same Circuit. . All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord, unless otherwise permitted in accordance with 300.3(B)(1) through (B)(4).
300.3(B)(2) Grounding and Bonding Conductors. . Equipment grounding conductors shall be permitted to be installed outside a raceway or cable assembly where in accordance with the provisions of 250.130(C) for certain existing installations or in accordance with 250.134(B), Exception No. 2, for dc circuits. . Equipment bonding conductors shall be permitted to be installed on the outside of raceways in accordance with 250.102(E).
250.130 ?.. For replacement of non-grounding-type receptacles with grounding-type receptacles and for branch-circuit extensions only in existing installations that do not have an equipment grounding conductor in the branch circuit, connections shall be permitted as indicated in 250.130(C). . [And (C) says to run the equipment grounding conductor to an grounding electrode conductor or to the service main for that specific limited situation only]
250.134(B) With Circuit Conductors. . By an equipment grounding conductor contained within the same raceway, cable, or otherwise run with the circuit conductors. . [I am under the impression that ?otherwise run? refers to 300.3(B) same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord]
Exception 1: nongrounding receptacle replacement
Exception 2: dc circuits
250.102(E) Equipment Bonding Jumpers. Installation. . The equipment bonding jumper shall be permitted to be installed inside or outside of a raceway or enclosure. . Where installed on the outside, the length of the equipment bonding jumper shall not exceed 1.8 m (6 ft) and shall be routed with the raceway or enclosure. . Where installed inside of a raceway, the equipment bonding jumper shall comply with the requirements of 250.119 and 250.148. . [250.119 is identification, 250.148 is connections]
My conclusions:
A) The last sentence of 300.3(B)(2) uses the term ? equipment bonding conductors? interchangeably with the term ?equipment bonding jumpers? in 250.102(E).
B) It?s interesting that 250.102(E) says the equipment bonding jumper shall comply with the requirements of 250.119 and 250.148. . And both of those references talk about the equipment grounding conductor.
C) It?s obvious that equipment bonding jumper and equipment grounding conductor are close to identical. . But 300.3(B)(2) definitely speaks of then in two separate sentences that have slightly different requirements.
There?s probably only a few possible differences. . I really didn?t want to suggest a definition. . I was hoping someone would step forward with a definite answer. . Since noone is interested in giving it a try, let me post the definition that I was told elsewhere and you tell me what you think:
DEFINITIONS
The equipment ground is a bonding jumper/conductor if:
it is outside of the raceway 6 ft or less and routed with raceway [250.102(E)] or non-electrode metal bonding [such as 250.104, 680.26(B), 680.43(D)],
or it is inside of a raceway that is 2 feet or shorter [Chapter 9 Notes to Tables(3)+(4)],
or both ends are terminated in the same enclosure [250.24(B), 250.30(A)(1)].
The equipment ground is a grounding conductor if:
it is outside of a raceway for nongrounding receptacle replacement or dc circuits [250.134(B)x1+2]
or it is inside of a raceway that is longer than 2 feet.
Gmack's IMO:
We cannot and should not tamper with the "fine line" as first described in the OP.
Why? Because if we do not keep them "blurred" together, we may open up a can that we do not want.
How? Because bonding will lose the ever needed "tie" to grounding all the way back to the main.
Consider that a electrician would only be concerned about bonding some "parts" and not be thinking of "ground".
Also IMO the NEC has to drive it again and again into everyones head that we ground the "grounded conductor" and it must be ever present that we "bond" the EGC's to it. At the main.
Going down a path of de linking for the sake of better english would be a mistake IMO.
2cents.