I have (6) 2" pvc conduits coming from a meter stack going to a common pullbox. From the pullbox I am taking MC to feed the unit panel in 6 different units. As I interpret 250.102 (d) [2nd paragraph] "A single common continuous equipment bonding jumper shall be permitted to bond 2 or more raceways or cables where the bonding jumper is sized......for the largest overcurrent device supplying the circuits therein."
The largest overcurrent device is 125a.
So as long as I take a #6 cu. conductor in one of the pvc conduits the box and the 6 MC cables are bonded properly. And it isn't necessary to pull a bond wire in each of the conduits to effectively bond the box and MC's.
The bond wire lands on a buss bar, which is also jumped to the pullbox, and the MC cable ground wires are also landed on that bus bar.
The single conductor is large enough to clear any ground fault likely to be imposed on it.
It certainly has caused a stir around here with people lining up on both sides. And of course the inspector doesn't like it.
And I don't think that induction would play much of a part in it.
let me hear some good arguments against it or for it.
The largest overcurrent device is 125a.
So as long as I take a #6 cu. conductor in one of the pvc conduits the box and the 6 MC cables are bonded properly. And it isn't necessary to pull a bond wire in each of the conduits to effectively bond the box and MC's.
The bond wire lands on a buss bar, which is also jumped to the pullbox, and the MC cable ground wires are also landed on that bus bar.
The single conductor is large enough to clear any ground fault likely to be imposed on it.
It certainly has caused a stir around here with people lining up on both sides. And of course the inspector doesn't like it.
And I don't think that induction would play much of a part in it.
let me hear some good arguments against it or for it.