250.104(A)(1)
augie47
Tennessee
In the '17 NEC the requirements for bonding metal waterr piping and structural steel reference 250.102(C)(1) without the 3/0 max exception which previously applied under 250.66. Have subsequent Codes or a TIA addressed that issue ??
Thanks. a 3/0 to bond an interior water line was, IMO, ridiculous but, larger, even more so.
Do you know if there was a TIA ??
Table T250.102(C) didn't change but, according to Texie, 250.104 has a max of 3/0 in 2020 whereas in 2017 it does not
(prior to 2017 it referenced 250.66 with the limit)
I think I see.... The 3/0 restriction is for water pipe bonding only. All other bonding can be larger than 3/0, if I read this correctly
(1) General.
Metal water piping system(s) installed in or attached to a building or structure shall be bonded to any of the following:
  • (1)
    Service equipment enclosure
  • (2)
    Grounded conductor at the service
  • (3)
    Grounding electrode conductor, if of sufficient size
  • (4)
    One or more grounding electrodes used, if the grounding electrode conductor or bonding jumper to the grounding electrode is of sufficient size
The bonding jumper(s) shall be installed in accordance with 250.64(A), 250.64(B), and 250.64(E). The points of attachment of the bonding jumper(s) shall be accessible. The bonding jumper(s) shall be sized in accordance with Table 250.102(C)(1) except that it shall not be required to be larger than 3/0 copper or 250 kcmil aluminum or copper-clad aluminum and except as permitted in 250.104(A)(2) and 250.104(A)⁠(3).