dana1028
Senior Member
- Location
- San Francisco Bay area
Scenario: Large commercial building going in [foundation stage]. The 2000A service is at one end of the structure, plastic water service is at the far end of the structure [300+ ft. away]; all interior water piping will be metallic [copper].
250.104(A)(1) says interior metal water piping systems shall be bonded and this can be achieved by bonding to an electrode.
The electrical contractor wants to use a 3/0 copper conductor and bond to the rebar at the far end of the building [i.e. 300+ ft. away from service location]....at the service location he will also use a 3/0 copper conductor to bond from the service equipment to the rebar.
As I understand the code, this is permissible and code compliant.
However, the inspector believes the purpose of interior water piping system bonding is to clear faults and does not feel 300+ ft. of rebar will provide the 'low-impedance path' necessary to clear a fault; thus he thinks a 3/0 conductor should be run from the interior metal water piping system directly back to the service to achieve this objective.
I understand the inspectors concern about the low-impedance path, but I also believe the contractor has met the code requirements with his bonding method.
Could I get some feedback please; both about whether the contractor's method is in fact code compliant and also addressing the low-impedance concern of the inspector.
[I also am an electrical inspector, but an observer in this issue].
250.104(A)(1) says interior metal water piping systems shall be bonded and this can be achieved by bonding to an electrode.
The electrical contractor wants to use a 3/0 copper conductor and bond to the rebar at the far end of the building [i.e. 300+ ft. away from service location]....at the service location he will also use a 3/0 copper conductor to bond from the service equipment to the rebar.
As I understand the code, this is permissible and code compliant.
However, the inspector believes the purpose of interior water piping system bonding is to clear faults and does not feel 300+ ft. of rebar will provide the 'low-impedance path' necessary to clear a fault; thus he thinks a 3/0 conductor should be run from the interior metal water piping system directly back to the service to achieve this objective.
I understand the inspectors concern about the low-impedance path, but I also believe the contractor has met the code requirements with his bonding method.
Could I get some feedback please; both about whether the contractor's method is in fact code compliant and also addressing the low-impedance concern of the inspector.
[I also am an electrical inspector, but an observer in this issue].