Stick, This is from the handbook following 104(A). Maybe it will help.
Bonding the metal water piping system of a building or structure is not the same as using the metal water piping system as a grounding electrode. Bonding to the grounding electrode system places the bonded components at the same voltage level. For example, a current of 2000 amperes across 25 ft of 6 AWG copper conductor produces a voltage differential of approximately 26 volts. Sections 250.104(A)(1) and (A)(3) require the metal water piping system of a building or structure to be bonded to the service equipment or grounding electrode conductor or, where supplied by a feeder or branch circuit, to the building or structure disconnecting means or grounding electrode conductor.