ceb58
- Raeford, NC
Replacing an old 100 amp service on a house with a 200 amp meter combo. I am going to feed the indoor panel, which is now a sub, with a 100 amp breaker in the combo. The house has NG lines ran in 3/4 black pipe and have never been bonded. I want to check to make sure I am right on this 250.104(B) states
The circuits would be from the 100 amp panel so by that I can use a #8 to bond the gas line. Correct? There is nothing else going to come from the combo to the house. They wanted the combo put in to feed a garage that will be built away from the house soon.
HTML:
The bonding conductor(s) or jumper(s) shall be
sized in accordance with 250.122, using the rating of the
circuit that is likely to energize the piping system(s).