Does the required bonding of structural steel in 250.104(C) make the steel a grounding electrode throughout the entire building?
 
More or less yes, usually you will use it as the electrode for all separately derived systems like transformers and generators.
 
Well, sort-of. If the bonding as required in section 250.104(C) satisfies one of the 4 requirements established in 250.52(A)(2), then YES.
 
Upon further reading, I see in 250.52(A) (2) (1) would be the only way that building steel itself would be considered an electrode.
 