A clarification please.
The SDS grounding electrode is required to use the same GES as the structure (250.30) and 250.104 requires bonding the SDS to the structural steel and water.
Do the exceptions to 250.104(D) mean that if the water and steel frame are connected to the service as part of the service GES that there is no need to bond the steel and water in the area of the SDS.
For example, IF I used the exception to 250.121 and used the EGC from my service as my SDS Grounding Electrode Conductor would I still need to bond steel and water in the area of the SDS even if they were part of the structure grounding electrode system ?