250.104
normbac
In a residence are there any codes that prohibit bonding to the gas pipe in the attic 250.104 says it needs to be accesssible. The inspector does not like the location, but there is an attic crawl space.
Seperate question in reading 250.104 (B) it seems to say that the bonding conductor should be based on branch circuit wires that may energize the pipe is that correct. Seems they are refering to individual circuits that may come in contact. I always thought it was based on the main panel feeders?
(The bonding jumper(s) shall be sized in accordance with 250.122 using the rating of the circuit that may energize the piping system(s).)
infinity
New Jersey
Journeyman Electrician
Around here the gas pipe is bonded indirectly by the EGC of the circuit supplying and bonding the gas appliance. So a gas boiler with a 15 amp circuit and a #14 EGC is all that's required to bond the gas pipe.
Cavie
SW Florida
I try to discourage it but it is accessible as per code.
normbac
walkerj said:
I bond it from the #12 or #14 from the outlet serving the furnace or water heater
Are you saying that you crimp a bare wire out of your outlet then bond it to the pipe?
Oops misread the post!!
Cavie
SW Florida
Manufacturer installations instructions call for flexible gas pipe to be bonded to the service by #6 sol wire.
Typically the gas pipe is bonded by the furnace since most places don't allow them to be connected w/fllex. The pipe connects to the gas valve which typically has a ground wire and the valve connects to a header which is screwed to the body of the furnace. But I've never heard that was allowed for the NEC bonding requirement.
normbac
How do you guys read the sizing in 250.104 (B) if gas pipe is in numerous locations in the attic and floor joists and wires of all sizes are near or touching are you taking the largest branch circuit and sizing it per 250.122
walkerj
Baton Rouge
I have seen it done that way.
or straight from the cold water pipe at the gas fired water heater.
I think a #6 is a little overkill though
walkerj
Baton Rouge
I read it as the largest egc from whatever circuits would enrgize it.
For instance, a flexible cord shorting out on the furnace. The #14 or #12 ground would clear the fault of that 15 or 20 amp circuit.
But i never run anything in close proximity to gas lines. I know it's not required, but gas + sparks + open air=bad news
Dennis Alwon
Chapel Hill, NC
Electrical Contractor
If one only has a gas range and it is plugged into a 15 or 20 amp receptace then the gas pipe is directly bonded thru that circuit. If the gas stove is unplugged then the bonding disappears. This seems odd to me.
I just heard that a local county here in NC is requiring bonding according to 250.66 for any gas piping in the building. Not just for the CSST piping.
normbac
So am I reading this incorrectly it seems to say the bond must be permanent
shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used.
electricmanscott
Boston, MA
The next time I install some flexible gas pipe I'll keep this in mind.
Otherwise if the installer of the gas pipe wants to hire me to bond their material per their instructions I'll worry about it then.
You CAN NOT cite 110.3 (B) for everything that is installed within a building ESPECIALLY when it is not even electrically related.
electricmanscott
Boston, MA
This is the correct answer for anybody under the NEC. No need to do anything else.
Dennis Alwon
Chapel Hill, NC
This is not always the case I have seen manufacturers info state that it shall be bonded per 250.66.
Edit to add
omegaflex said:
H. Protection for Gas Piping Systems in High Lightning Strike Regions
omegaflex said:
TracPipe CounterStrike
Model Number(s) FGP-CS-375 FGP-CS-500 FGP-CS-750
FGP-CS-100 FGP-CS-125 FGP-CS-150 FGP-CS-200
H.1 Primary protection from lightning near strikes for all metallic systems within a
building is recommended to be provided by proper grounding of the electrical
system and equipotential bonding of all metallic systems including the gas piping
system. Grounding and bonding shall be in accordance with the National
Electrical Code ANSI/NFPA 70.
H.2 The installation of a lightning protection system per NFPA 780 is
recommended in areas prone to a high level of lightning strikes to protect the
building In the event of a direct strike.
H.3 CounterStrike shall consist of TracPipe stainless steel pressure liner and
an engineered polymer jacket. The jacket shall be designed to enhance the
energy dissipating properties of the flexible gas piping. CounterStrike shall be
tested by a recognized lightning laboratory. In lightning prone areas,
Counterstrike is recommended for an additional level of gas piping system
protection from indirect strikes.
H.4 The use of CounterStrike shall be coupled with equipotential bonding of the
gas piping system and all other metallic systems to the grounding electrode in
accordance with NEC Section 250.104. The bonding jumper should be sized in
accordance with NEC Table 250.66
walkerj
Baton Rouge
What if the gas line only serves gas lanterns or straight gas water heaters, nothing gas with elec. ignitors. What should be done in that case?
normbac
So if you have a oven that is say 40 amp are you suppose to run a # 10 from the outlet or panel etc; per table 250.122 to wherever it can be accessible? Need clarity on this so I can argue my point to an inspector TIA
Cavie
SW Florida
Can I ask why you do this and where you get the authority to do so?
I simply sugest it be done in a more accessable mannor and most do not complain and agree. I do not insist it not be done. It is accessable in the attic.