In a residence are there any codes that prohibit bonding to the gas pipe in the attic 250.104 says it needs to be accesssible. The inspector does not like the location, but there is an attic crawl space.
Seperate question in reading 250.104 (B) it seems to say that the bonding conductor should be based on branch circuit wires that may energize the pipe is that correct. Seems they are refering to individual circuits that may come in contact. I always thought it was based on the main panel feeders?
(The bonding jumper(s) shall be sized in accordance with 250.122 using the rating of the circuit that may energize the piping system(s).)
Seperate question in reading 250.104 (B) it seems to say that the bonding conductor should be based on branch circuit wires that may energize the pipe is that correct. Seems they are refering to individual circuits that may come in contact. I always thought it was based on the main panel feeders?
(The bonding jumper(s) shall be sized in accordance with 250.122 using the rating of the circuit that may energize the piping system(s).)