250.106 Lightning Protection Systems.
"The lightning protection system ground terminals shall be bonded to the building or structure grounding electrode system."

To comply with 250.106, I typically specify rods to ground either the building or lightning protection system and a ring to ground the other with a bonding jumper between each rod and the ring. Alternatively, each lightning protection ground terminal could be bonded to structural steel.

A colleague has suggested after reading NFPA 780, that this is unnecessary. He insists that we only need a single bonding between a lightning protection conductor and the facility's main grounding bar.

Our debate is about how literally to take 250.106.

Does 250.106 require the direct bonding of each ground terminal or is a single bonding adequate for the entire system?
 

bphgravity

Senior Member
Location
Florida
It appears your colleague is referring to Section 4.14.5 in the NFPA 780 which allows ONE connection to other building grounded systems.
 
I have always practiced compliance with the most stringent applicable code.

I wish 250.106 was the following:
"The lightning protection system shall be bonded to the building or structure grounding electrode system according to NFPA 780."
 