lpfink
Member
- Location
- San Diego, CA, USA
We use MC-HL in Class 1 Div 2 locations on our equipment and use two different MC-HL cables. Both use a corrugated metallic sheath but the 1st type is filled with single conductors and includes a green insulated wire (wire type EGC) and the 2nd type contains twisted pairs or twisted triads with shielding and a drain wire for each pair or triad, along with an overall shielding and drain wire. My questions are related to 250.118(10):
1) Is there any MC cable where the metallic sheath ALONE is suitable to be used as the EGC? Seems like 250.118(10)(c) says there is if the metallic sheath is listed and identified as an EGC.
2) Brings me to my next question. UL1569 (Standard for Metal Clad Cables) section 6.1.8 says if the resistance of the metallic sheath is equal to or below on of the values in Table 6.1 - 6.4 it MAY contain an EGC, leading me to believe that the sheath ALONE is suitable as the EGC. The other sections of UL 1569 say SHALL contain.... Would a MC cable meeting UL 1569 be meeting the requirement from 250.118(10)(c) of being listed and identified?
Here is section 6.1.8 from UL 1569:
3) How would the requirements to bond/ground apply to the instrumentation cable MC-HL we are using, if you guys have any input. Put another way, wouldn't this type of cable need a combined wire type/metallic sheath if the metallic sheath ALONE wasn't suitable to serve as the EGC?
I will ask our supplier for the certificate of compliance to see if anything is mentioned but from our drawings I don't see anything. Thanks!!
1) Is there any MC cable where the metallic sheath ALONE is suitable to be used as the EGC? Seems like 250.118(10)(c) says there is if the metallic sheath is listed and identified as an EGC.
2) Brings me to my next question. UL1569 (Standard for Metal Clad Cables) section 6.1.8 says if the resistance of the metallic sheath is equal to or below on of the values in Table 6.1 - 6.4 it MAY contain an EGC, leading me to believe that the sheath ALONE is suitable as the EGC. The other sections of UL 1569 say SHALL contain.... Would a MC cable meeting UL 1569 be meeting the requirement from 250.118(10)(c) of being listed and identified?
Here is section 6.1.8 from UL 1569:
3) How would the requirements to bond/ground apply to the instrumentation cable MC-HL we are using, if you guys have any input. Put another way, wouldn't this type of cable need a combined wire type/metallic sheath if the metallic sheath ALONE wasn't suitable to serve as the EGC?
I will ask our supplier for the certificate of compliance to see if anything is mentioned but from our drawings I don't see anything. Thanks!!