Does this mean I can take a 14/3 uf and mark the red conductor at either end green and use it where the ecg shall be insulated due to application
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Yes you can.

I prefer to just strip the red insulation off the wire and then you are good to go for an equipment grounding conductor.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Are you asking about re-identifying a red conductor as an insulated EGC for something like a pool circuit?
 