250.119 2 B 2020 nec

Status
Not open for further replies.

Camden123

Member
Location
Louisa Va
Occupation
Electrician
Does this mean I can take a 14/3 uf and mark the red conductor at either end green and use it where the ecg shall be insulated due to application
 
Yes you can.

I prefer to just strip the red insulation off the wire and then you are good to go for an equipment grounding conductor.
 
Are you asking about re-identifying a red conductor as an insulated EGC for something like a pool circuit?
 