250.120(c)

Status
Not open for further replies.

tbro723

Member
Does this section apply to EGC's for solar panel frame grounding in ground mount and carport structure applications? I think it is a question of code interpretation whether the ground conductor is physically protected from physical damage. There are even those Tyco Solklips that can only accept a #10-12 ground anyway so having to use a #6 would not even make sense. Any thoughts, inputs, suggestions?
 
I'm not really sure what the question is, or what in particular you feel needs commenting on...

The requirement is IMO pretty clear cut regarding an EGC < 6AWG. It does not say only if it IS subject to physical damage. It says it must be protected from physical damage... period.

If it is in a wall or otherwise encased by a structural element (perhaps even buried), or within armored cable, or inside a raceway, it is protected. If you can see or touch it (or its insulation if insulated), it is not protected.

If you feel doing so in a particular situation is impracticable, please provide a detailed description (and/or one or more pictures).
 
I'm not really sure what the question is, or what in particular you feel needs commenting on.

I believe he is referring to bonding the solar panels together; it is common to run a bonding jumper [sized the same as the circuit conductors] to the undersize of each panel 'unprotected'...i.e. not in conduit.

That said, this is an installation unlikely to encounter physical damaged and in my area I don't know that 'protecting' the bonding conductor has ever been required.

Is a bonding conductor required to be protected?

tbro: if you are really losing sleep over this, contact John Wiles [the PV guru] at Southwest Tech Devel. Institute - Univ. of New Mexico.
www.nmsu.edu/~tdi
 