250.121 exception

Status
Not open for further replies.

Epalmateer

Senior Member
Location
Michigan
Occupation
Electrician
200 amp service. Feed through panel to 150a subpanel. Would 250.121 exception allow me to run gec from water meter to sub panel?
 
No. And how are you feeding a 150 amp panel from a 200 amp feed though?
Meant 150 amp main panel. Sorry about that. What would not allow it? It says if the egc meets the requirements of the egc and gec it could be used as both. 250.64 (d)(2)(2) makes me think you can. I'm by no means arguing, just discussing.
 
Imo, if the equipment grounding conductor is the correct size and you have an irreversible connection on the equipment grounding conductor then it would be allowed.
 
If you have the right tool you can do it... or a cad weld....

shopping
shopping
shopping
 
Imo, if the equipment grounding conductor is the correct size and you have an irreversible connection on the equipment grounding conductor then it would be allow

Imo, if the equipment grounding conductor is the correct size and you have an irreversible connection on the equipment grounding conductor then it would be allowed.
Would 250.8 a 2 allow you to just connect it to the ground bar in the sub panel?
 