Dennis, I don't see an ambiguity here. Let me invite your attendtion to the fact that 250.122(A) does not say that the EGC need not be larger than the circuit conductors in the same raceway. It says the EGC need not be larger than the circuit conductors supplying the equipment. In your example, the circuit conductors supplying the equipment consist of seven 1/0's, so the EGC need not be larger than that. I think the present wording is clear enough, provided that the reader read all the words. Charlie's Rule wins again!
But, (F) requires a 2/0 in each conduit. seven 2/0's is larger than seven 1/0's. Does (A) prevail and only require 1/0's in the conduits, or does (F) prevail and require 2/0's in the conduits? I think, since (F) is a more specific rule, it prevails.