I may never see 2014 adopted in this area but sometimes it's difficult to explain 250.122(B) to folks when they increase phase conductors foe any reason, the EGC must be proportionally addressed.
2014 has changed the wording of 250.122(B) and I don't fully understand the change.
Does it take us back to the days where EGC increases were only need for conductor increases for voltage drop ?
2014 has changed the wording of 250.122(B) and I don't fully understand the change.
Does it take us back to the days where EGC increases were only need for conductor increases for voltage drop ?