mdshunk
Senior Member
- Location
- Right here.
When I have a PVC conduit and junction boxes that all contain 20 amp circuits, but some of them have been upsized to overcome voltage drop, how do I size the EGC? Some of the conductors are #4, which would seem to require #4 ground in accordance with 250.122(B) which says "shall be increased in size...". Now, since there are multiple conductors in this conduit and boxes (all 20 amp), 250.122(C) seems to indicate only a #12 ground. It says, " shall be sized for the largest overcurrent device.". How do I size when both articles apply and both say " shall be"?? Other than one article requireing a larger EGC, there doesn't seem to be any "tie breaking" article in the code that would require me to pick the larger one. Obviously, good sense would cause me to pick the larger one, but the code doesn't seem to make that choice for me clear.