I was just reading Ryan's post about raceways used as grounding means and I thought about 250.122(B), yes I know, I have to get a life.
Lets say you have post lights at the end of a long driveway.
The total load is 10 amps @ 120 volts, the length is 500' and you decide you want to keep the voltage drop to less than 5%.
This will mean you must run 6 AWG for the line conductors.
What size grounding conductor will be required, based on a 15 amp breaker?
Will you be able to use 6/2 UF cable out to the lights?