This paragraph is so poorly written, I can't believe it stands! There are so many situations where there is no benefit or justification to increase the grounding conductor size just because the ungrounded conductors are sized larger. In what universe does it make sense that 50 foot run of 3-3/0 THWN and a #6 ground are OK for a 200A breaker, but change the breaker to 150A and the ground has to somehow be larger? Or A metal conduit run where I can pull the ground out of the conduit and be legal, but if I leave it in, it needs to increase in size?
That is a rant however. Coming up against this code section yet again, I had a couple other questions that it doesn't properly address. First, when are the ungrounded conductors considered increased? If, for example, I don't take advantage of the 240.4 exception, is that increasing the size? If I don't have proof that the lugs are rated at 75º so I use the 60º table then find out later that the lugs are rated at 75 have I violated the code because my conductors are larger?
So on a serious note. In your opinion, can we use the 60º table ampacities and the actual current rating without taking exception 240.4 to determine whether the conductors are oversized? If not, why not? Take the 1/0 example. If I use the 75º table to determine the ampacity, then the ground must be increase to #4. If I use the 60º table which has the exact same cross section of current carrying copper, then I can go all the way down to a 125A breaker without oversizing the ground conductor.
That is a rant however. Coming up against this code section yet again, I had a couple other questions that it doesn't properly address. First, when are the ungrounded conductors considered increased? If, for example, I don't take advantage of the 240.4 exception, is that increasing the size? If I don't have proof that the lugs are rated at 75º so I use the 60º table then find out later that the lugs are rated at 75 have I violated the code because my conductors are larger?
So on a serious note. In your opinion, can we use the 60º table ampacities and the actual current rating without taking exception 240.4 to determine whether the conductors are oversized? If not, why not? Take the 1/0 example. If I use the 75º table to determine the ampacity, then the ground must be increase to #4. If I use the 60º table which has the exact same cross section of current carrying copper, then I can go all the way down to a 125A breaker without oversizing the ground conductor.