I have load of 290A. The breaker used is 300A breaker. The cable size used due to voltage drop is 500kcmil cu at 75C
Equipment grounding conductor should be increased but what would be the minimum intended size cable be for 250.122(B)? Anyone know?
The engineer is saying minimum cable size is 300kcmil not 250kcmil cu at 75C. Is he correct or incorrect?
Equipment grounding conductor should be increased but what would be the minimum intended size cable be for 250.122(B)? Anyone know?
The engineer is saying minimum cable size is 300kcmil not 250kcmil cu at 75C. Is he correct or incorrect?