250.122(B) revision
bphgravity
Florida
1. 250.122(B)
2. Add Text (In Italics)
3. (B) Increased in Size. For circuits rated greater than 60-amperes, and where ungrounded conductors are increased in size, equipment grounding conductors, where installed, shall be increased in size proportionately according to circular mil area of the ungrounded conductors.
4. For circuits rated under 30-amperes, increasing the EGC in proportion to the ungrounded conductor is unnecessary and results in the EGC being larger than what would be required for circuits using the same conductors on higher circuit ratings. For example, #10 AWG conductos are increased in size to #8. Per the current 2005 wording of the section, the EGC would be required to be increased to #8 as well. However, the same #10 AWG conductors could be used on a 40-ampere branch circuit with a #10 AWG EGC. If a #10 AWG EGC is sufficent for a 60-ampere circuit, where #6 AWG conductors are used for ungrounded conductors, why wouldn't #10 AWG EGC be sufficent on a 30-ampere circuit where #10 AWG conductors are used for ungrounded conductors.
We have had this discussion on this Forum several times and think this issue merits a change.
Re: 250.122(B) revision
OK Bryan, suppose you are running #6 Cu 3/C / #10 Ground for a long 60 ampere feeder and need to upsize the circuit conductors to #2 Cu, why wouldn't you need to upsize the #10? If the feeder was really that long to need to be that large, the grounding conductor would surely need to be larger as well to be effective. :D
Okay, I agree. There is definitely a problem with this requirement under certain conditions. I just can't seem to figure out how to correct that issue.
There must be a way to make the point that when certain conductors are increased to a certain size, the EGC may not need to be increased if it does not exceed the size shown in Table 250.122 for a circuit at ratings under 60-amperes.
I will give it more thought, thanks.
bph - I know what you are getting at but I do not know how to word it either.
I got into a situation where needed to run #6 for voltage drop using 30A branch ckts. for very long underground runs to parking lot light poles. Each pole had (4) 1000W HID luminaires.
Do not remember exactly, but seems like I felt compelled to use #6 EGC also.
Obviously #8 or even #10 EGC would have made it a little bit easier.
Bryan, for what it is worth, I agree with you. I think a little background is important though. The original table was set up to permit the size of grounding conductor that was really needed. Therefore, the #14 and #12 would have about a #16 grounding conductor, the #10 was a lot bigger and it was about a #14. A lot of people were not accustomed to using the grounding conductor for grounding and started to use them for a neutral or even for 3-way switches. At that point, the proposal was to change to a full size grounding conductor until you got to a 40 ampere circuit.
If you went back far enough to get the original sizes for a starting point for increasing with the present size as the minimum after calculations, that may work. I see this method as being very clunky though. Kinda reminds me of derating and using the 90?C for the starting point and then the rating of the equipment for the maximum ampacity.
I wonder if we really want to introduce another complicated (to a lot of people) method into the Code? :D