NOV
Member
- Location
- Upstate NY
- Occupation
- IDC Electrical Review Engineer
I'm looking at a set of drawings which has an 800A distribution panel fed with (5) parallel feeders of 500KCMIL. The feeder has a Key Note stating it was upsized due to voltage drop. The Feeder Schedule lists the feeder with a #1/0 grounding conductor which doesn't meet 250.122(B). In order to size the grounding conductor for this, am I correct in thinking I have to divide 800 by 5 (160) and use that corresponding conductor (#2/0) circular mil area to calculate the percentage the ungrounded conductor was increased? Then of course increase the grounding conductor by that percentage.