250.122 (B)

Status
Not open for further replies.

jbolen

Senior Member
We install 10/2 w ground MC Cable for voltage drop for a 20-amp receptacle 20 circuit breaker. Can we use a #12 ground pigtail to the box.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
What about having to increase the EGC the same ratio as the ungrounded conductors?
I thought about that. There are no corresponding circuit conductors for the pigtail jumper.

Added: Also, there would be no voltage drop attributed to a 6" long wire.
 