Statement: This has been revised from the 2005 code.
From the Code: Where conductors are run in parallel in mutiple raceways or cables as permitted in 310.4, the equipment grounding conductors, where used, shall be run in parallel in each raceway or cable.
Example: I have a 800 amp feeder. Using 3-3C/350MCM w/gnd, XHHW-2 Rounted in tray with 3-3" conduits on each end to drop into the switchgear and into a
mcc. Aprox 3' lenghts of conduit on each end.
Per code the equipment grounding conductor for an 800 amp protective device is an 1/0 copper. The standard equipment conductor within a 3/c350mcm w/gnd is a #3 awg. This is therfore not adequate.
Are the following valid options?
1. Order special cable with correct size EGC. (yes)
2. use 3-3c350mcm w/no ground and pull a seperate (1)- 1/0 EGC in cable tray from point A to point B in a seperate conduit???
3. Pull (3) - 1/0 EGC in cable tray from point A to point B and route in the 3conduits with the phase conductors even though they are only short conduit drops. Since the code says in each raceway
Also, since the code say IN cable is a seperate external ECG cable acceptable or does it have to be part of the multi-conductor cable?
From the Code: Where conductors are run in parallel in mutiple raceways or cables as permitted in 310.4, the equipment grounding conductors, where used, shall be run in parallel in each raceway or cable.
Example: I have a 800 amp feeder. Using 3-3C/350MCM w/gnd, XHHW-2 Rounted in tray with 3-3" conduits on each end to drop into the switchgear and into a
mcc. Aprox 3' lenghts of conduit on each end.
Per code the equipment grounding conductor for an 800 amp protective device is an 1/0 copper. The standard equipment conductor within a 3/c350mcm w/gnd is a #3 awg. This is therfore not adequate.
Are the following valid options?
1. Order special cable with correct size EGC. (yes)
2. use 3-3c350mcm w/no ground and pull a seperate (1)- 1/0 EGC in cable tray from point A to point B in a seperate conduit???
3. Pull (3) - 1/0 EGC in cable tray from point A to point B and route in the 3conduits with the phase conductors even though they are only short conduit drops. Since the code says in each raceway
Also, since the code say IN cable is a seperate external ECG cable acceptable or does it have to be part of the multi-conductor cable?