250.122

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Construction put 3, 500kCMIL, per phase along with 3 EGCS is a single 6” RGS conduit from an undersized pull box to the panelboard - the conduit is only about 2’ long - is this a code violation?


Sent from my iPhone using Tapatalk
 
Last edited:

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Besides the undersized pull box there is no violation to have multiple EGC's.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Besides the undersized pull box there is no violation to have multiple EGC's.

Is there a problem with having 9 , 500kCMIL in a single conduit (3 per phase) as long as derating is applied?


Sent from my iPhone using Tapatalk
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
No fill problem and if the nipple is not over 24" long, no derating required.

These are single conductors, 500kCMIL 3 per phase. Is there any concern with inductance and hot spots if they’re all laid in the same conduit?


Sent from my iPhone using Tapatalk
 

SSDriver

Senior Member
Location
California
Occupation
Electrician
They only need one EGC but I'm assuming this was there transition from parallel runs. If so each EGC needs to be sized as a full EGC.
 

SSDriver

Senior Member
Location
California
Occupation
Electrician
Can you elaborate on why not? Is this because of the short distance or simply because the insulation is sufficient protection?


Sent from my iPhone using Tapatalk
Nipples 24" and under do not require derating of conductors.

310.15c states derating is for lengths longer than 24"
 

SSDriver

Senior Member
Location
California
Occupation
Electrician
Understood but my question is not about derating


Sent from my iPhone using Tapatalk
Then what would be the problem.

Conductance - no, all circuit wires are in the same conduit.

Heating- no, nipple is too short to contain any heat build up hence why nipples shorter than 24" don't require derating.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
These are single conductors, 500kCMIL 3 per phase. Is there any concern with inductance and hot spots if they’re all laid in the same conduit?
No, parallel conductors are permitted in a single raceway. Since you're not more than 24" no sweating applies. Fill can be up to 60% so that's not an issue either.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
No parallel conductors are permitted in a single raceway. Since you're not more than 24" no sweating applies. Fill can be up to 60% so that's not an issue either.

Thanks infinity
“No parallel conductors are permitted in a single raceway”
Where exactly is that found?
(Using 2023 NEC)


Sent from my iPhone using Tapatalk
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
No parallel conductors are permitted in a single raceway. Since you're not more than 24" no sweating applies. Fill can be up to 60% so that's not an issue either.

If the 24” nipple is considered a raceway, is this a code violation?


Sent from my iPhone using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
310.10(H) addresses conductors in parallel and the wording allows them to be in the same conduit.
As noted above, 310.15.(B)(3)(a) addresses derating and notes derating is not necessary when the raceway is 24" or less in length/
Chapter 9, Table 1 will confirm there is no problem with fill.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
310.10(H) addresses conductors in parallel and the wording allows them to be in the same conduit.
As noted above, 310.15.(B)(3)(a) addresses derating and notes derating is not necessary when the raceway is 24" or less in length/
Chapter 9, Table 1 will confirm there is no problem with fill.

I don’t find 310.10(H) in either 2020 or 2023.
What concerns me is 366.20 which requires conductors in parallel to be separate groups to prevent current imbalance due to inductive reactance
Does this apply to a short conduit nipple?


Sent from my iPhone using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
In 2020, it's 310.15(G)
With all your conductors sharing the nipple, they would be grouped as required by 366
 