A electrician has installed a piece of 1/2" pvc schedule 40 combined with a 2.5 foot section of FMC to protect a run of 10-2 romex. The FMC ended with a angle connector at a wall and did not terminate on a metal box or raceway.
334.15(B) does not mention schedule 40 PVC as suitable supplementary protection.
The 30" piece of flex that goes between pvc and the wall where the 10-2 emerges into the wall is not bonded on either end. Granted it is just supplementary protection.
Now we do have:
Opinions?
Similar situations?
I had to cut the 1/2" PVC lb in half to remove the 10-2 and can hardly believe it would not be a raceway fill violation to even install 10-2 romex in 1/2" pvc.
Does 300.12 ex 1 exempt the "short" section of raceway from being bonded as required by 250.132?
334.15(B) does not mention schedule 40 PVC as suitable supplementary protection.
The 30" piece of flex that goes between pvc and the wall where the 10-2 emerges into the wall is not bonded on either end. Granted it is just supplementary protection.
And 300.10nec-2011 said:250.132 Short Sections of Raceway
Isolated sections of metal raceway or cable armor, where re-
quired to be grounded, shall be connected to an equipment
grounding conductor in accordance with 250.134.
Seems to require the flex to have had a bonding bushing IMO.Metal raceways, cable armor, and other metal enclosures for
conductors shall be metallically joined together into a continuous
electrical conductor and shall be connected to all
boxes, fittings, and cabinets so as to provide effective electrical continuity.
Now we do have:
However it does not say bonded, just that it does not have to be a complete system.300.12 ex1" said:Exception No. 1: Short sections of raceways used to pro-
vide support or protection of cable assemblies from physical
damage shall not be required to be mechanically continuous.
Opinions?
Similar situations?
I had to cut the 1/2" PVC lb in half to remove the 10-2 and can hardly believe it would not be a raceway fill violation to even install 10-2 romex in 1/2" pvc.
Does 300.12 ex 1 exempt the "short" section of raceway from being bonded as required by 250.132?