250.134 " if grounded, shall be connected to equipment grounding conductor."
250.134
what is the intent of it stating "..., if grounded, shall be connected to an equipment grounding conductor..."?
(and right after 250.134) when you look at 250.136 "equipment considered grounded" and 250.136(A) after reading that 250.134 part, it about sounds like anything on the rack should get it's own EGC. but then explanatory material in handbook says it's good without individual EGC's, just one for the rack.
whats your thoughts?
are they just saying don't use neutral or GEC as a means of equipment grounding, except where allowed to use neutral. is it just me or could this use some cleaning up?
Thanks
250.134
what is the intent of it stating "..., if grounded, shall be connected to an equipment grounding conductor..."?
(and right after 250.134) when you look at 250.136 "equipment considered grounded" and 250.136(A) after reading that 250.134 part, it about sounds like anything on the rack should get it's own EGC. but then explanatory material in handbook says it's good without individual EGC's, just one for the rack.
whats your thoughts?
are they just saying don't use neutral or GEC as a means of equipment grounding, except where allowed to use neutral. is it just me or could this use some cleaning up?
Thanks