• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

250.136 bonding a steel switch rack

Merry Christmas

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
At this site, they are insisting the metal switchbacks must be bonded to an equipotential plane that is buried approximately 18” deep. Per 250.136,
I’ve told them that if the rack is bonded via the EGC to the main disconnecting means there is no need to provide an additional bond from metal rack to the so called “grounding loop”.
Am I missing something here?


Sent from my iPhone using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
At this site, they are insisting the metal switchbacks must be bonded to an equipotential plane that is buried approximately 18” deep
What are metal switchbacks? Your title says racks are you asking about a strut rack used to support disconnect switches?
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
Most industrial oil/gas plants always require us in there specs for everything electrical to be bonded to the “grounding grid”
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Most industrial oil/gas plants always require us in there specs for everything electrical to be bonded to the “grounding grid”

Yea but this is not an oil and gas project. Also my understanding is the grounding grid is a standard practice and not a Code requirement


Sent from my iPhone using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Thanks Infinity. That’s what I thought
Even if you considered the strut or rack likely to become energized you would bond it to the EGC not an equipotential plane. 250.136 which takes you to 250.134 confirms this.
 
Top