A/A Fuel GTX
Senior Member
- Location
- WI & AZ
- Occupation
- Electrician
I've got a situation where an existing 3 wire dyer circuit needs a new receptacle installed along with the dryer cord itself. Originally this circuit was dervived from the service equipment however due to a new service being installed, the circuit now is supplied by a sub panel. The new meter section has a main breaker as part of it so the old service equipment is now a sub panel. In reading the requirements of 250.140, to use an existing circuit it must be originated from the service equipment. Due to accessibilty issues, it would be very difficult to run a new 4 wire branch circuit to this location. There are no parallel path issues here because SE-R is run to the sub panel and NM cable is run to the original dryer receptacle. Am I OK to just replace the cord and receptacle and keep the dryer bonded to the grounded conductor?