San -Brooke
Member
- Location
- USA
If a receptacle is being fed through a raceway that does in fact meet NEC requirements as providing EGC (such as EMT,Rigid, IMC etc...) from the supply(panel board) to a box then why would you ever require to bond to the box(4x4, FS, bell box, etc...) if you pull a ground wire to the device? If you refer to the NEC hanbook on page 277 exhibit 250.59 it illustrates an IG receptacle with a grounding conductor going directly to the device and illustrates the metal raceway(EMT and box) as providing a suitable grounding means without pulling a second grounding conductor. So if that is the case then why would it be necessary to gound to the box just because you would have continuity between the receptacle and yoke?