I want to get an opinion on a bonding issue that I have run into in a multifamily high rise building. Each condo unit has a split mechanical system with a condenser located on the roof. The rooftop condensers are fed from each individual condo unit in a number of typical electrical risers. The condensers feeders in a typical riser terminate at the roof in terminal blocks within a NEMA 3R metal enclosure. These feeders will change to L/T Flex conduit and continue on to each individual condenser. I have a question concerning 250.148 that says that circuits spliced or terminated in a metal box will have to have to associate EGC's connected to the box.
Would we be creating a problem by effective connecting all the grounds together in the described enclosure per 250.148, when many of the circuits originate from separately derived systems? If a condo unit lost its means of ground at the unit panel and then had a fault, would the fault not continue up this riser and possible dissipate onto the grounds of the other condo units? I am open to any comments concerning this issue.
Thanks,
Jerry
Would we be creating a problem by effective connecting all the grounds together in the described enclosure per 250.148, when many of the circuits originate from separately derived systems? If a condo unit lost its means of ground at the unit panel and then had a fault, would the fault not continue up this riser and possible dissipate onto the grounds of the other condo units? I am open to any comments concerning this issue.
Thanks,