250.166(B) DC GEC

Status
Not open for further replies.

NorthwestPV

Member
Location
Oregon, US
In Article 250.166(B), it says the grounding electrode conductor shall not be smaller than the largest conductor supplied by the system.

I have a project with a 400 Amp service. Its GEC consists of a #6 Cu ran to two ground rods. I have 2 DC sets of #4 running to a combiner box. It is my understanding that the DC GEC must equal the sum of the DC conductors which would be a 1/0 Cu GEC. The NEC only requires a #6 to the ground rods no matter how large the service is. Do I really need to run a 1/0 to the existing ground rods? My feeling is I should only have to run a #6. Am I wrong in my thinking?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I don't think you're wrong (except that nowhere in the NEC does it suggest that the sum of DC conductors must be used, just the largest single conductor. So it is between #6 and #4, not #6 and 1/0).

You can use a #6. Note 250.166(C) contravenes (B) with respect to rods.

We just discussed pretty much the exact same thing yesterday in the PV forum. http://forums.mikeholt.com/showthread.php?t=147317

See also 690.47.
 