- Location
- Baton Rouge
- Occupation
- Electrical Inspector
We have 1/C 15kV, 3 Phase feeders coming from an outdoor utility substation SF6 CB. They run underground direct buried to a 3MVA XFMR Primary w/480V secondary which feeds a 480V switchgear. The MV cable is not MC cable BUT it does have a shield. Looking at 250.190 and 240.100, it looks like I can use the shield as an EGC; we have Schweitzer relays for protection and the upstream transformer 69kV to 13.8kV has a resistor. Do I still need to run a separate EGC with with the phase conductors or will the shield suffice?