250.190 and 250.100

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
We have 1/C 15kV, 3 Phase feeders coming from an outdoor utility substation SF6 CB. They run underground direct buried to a 3MVA XFMR Primary w/480V secondary which feeds a 480V switchgear. The MV cable is not MC cable BUT it does have a shield. Looking at 250.190 and 240.100, it looks like I can use the shield as an EGC; we have Schweitzer relays for protection and the upstream transformer 69kV to 13.8kV has a resistor. Do I still need to run a separate EGC with with the phase conductors or will the shield suffice?


Sent from my iPhone using Tapatalk
 
We have 1/C 15kV, 3 Phase feeders coming from an outdoor utility substation SF6 CB. They run underground direct buried to a 3MVA XFMR Primary w/480V secondary which feeds a 480V switchgear. The MV cable is not MC cable BUT it does have a shield. Looking at 250.190 and 240.100, it looks like I can use the shield as an EGC; we have Schweitzer relays for protection and the upstream transformer 69kV to 13.8kV has a resistor. Do I still need to run a separate EGC with with the phase conductors or will the shield suffice?


Sent from my iPhone using Tapatalk
Is the 13.8 system a delta or wye system? MGN? Where is the service point? What kind of shield does the cable have?
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Is the 13.8 system a delta or wye system? MGN? Where is the service point? What kind of shield does the cable have?

System, incoming service is 69kV Delta-Wye with neutral resistor on the secondary of the power transformers. Power originates from a local power plant.
Cable is Okonite Okoguard-MV-105 15kV Shielded Power Cable
Copper Conductor/105°C W/133% Insulation Level
Shield is 5 mil bare copper tape helically ap- plied with 12.5% nominal overlap. The protective relays have all the bells and whistles including 50/51, 87, 27 etc


Sent from my iPhone using Tapatalk
 
System, incoming service is 69kV Delta-Wye with neutral resistor on the secondary of the power transformers. Power originates from a local power plant.
Cable is Okonite Okoguard-MV-105 15kV Shielded Power Cable
Copper Conductor/105°C W/133% Insulation Level
Shield is 5 mil bare copper tape helically ap- plied with 12.5% nominal overlap. The protective relays have all the bells and whistles including 50/51, 87, 27 etc


Sent from my iPhone using Tapatalk
It does seem that if the 15kv system is not solidly grounded then you could use the tape shield as the EGC. I assume you have researched whether the shield is rated for the fault current?

Just curious, is the 13.8 to 480 transformer delta wye?
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
It does seem that if the 15kv system is not solidly grounded then you could use the tape shield as the EGC. I assume you have researched whether the shield is rated for the fault current?

Just curious, is the 13.8 to 480 transformer delta wye?

Yes - and the 13.8kV to 480V is delta wye.
Many thanks
Isaiah


Sent from my iPhone using Tapatalk
 