m sleem Top-notch Сasual Dating - Real-life Females Location Usa Occupation Health Apr 20, 2020 #1 Where is the service panel's grounding bar in first exhibition? compared to second one where both are 3-phase, 4-wire, wye connected system.
Where is the service panel's grounding bar in first exhibition? compared to second one where both are 3-phase, 4-wire, wye connected system.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Apr 20, 2020 #2 They're each in the service disconnect. The second example has separate neutral and grounding bars with a bonding jumper between them, while there is only one bar in the first example. What's different to you that prompts you to ask the question?
They're each in the service disconnect. The second example has separate neutral and grounding bars with a bonding jumper between them, while there is only one bar in the first example. What's different to you that prompts you to ask the question?