250.24(A)(2) Outdoor Transformer. Where the transformer supplying the service is located outside the building, at least one additional grounding connection
shall be made from the grounded service conductor to a grounding electrode, either at the transformer or elsewhere outside the building.
I assume this rule simply requires to drive ground rods at utility xfmr location and then bond the xfmr secondary neutral to the ground rods?
I don't recall I have seen this installation at any sites where there is a pad mounted utility xfmr. Am I missing something?