This section allows the grounded conductor to be bonded at two locations, one at the utility's outdoor transformer and the second at the service disconnecting means of my building.
Now if my utility is providing me with a medium voltage (primary voltage) service,and I then distribute it through out the site and step it down to 480/277V Y at each of the many buildings in my site, is it a code violation to bond the neutral at the transformer AND at the building disconnect? (it will basically be the same as if the utility provided me with a 480/277V Y service directly to my building)
Now if my utility is providing me with a medium voltage (primary voltage) service,and I then distribute it through out the site and step it down to 480/277V Y at each of the many buildings in my site, is it a code violation to bond the neutral at the transformer AND at the building disconnect? (it will basically be the same as if the utility provided me with a 480/277V Y service directly to my building)