I have a dispute with one of my contractors about the termination point of the GEC, and want to get some interpretations of 250.25(A)(4).
What I have is 600-amp service disconnect enclosure with 4-wire, 3-phase 208Y/120. There is an insulated neutral bus on one side of the cabinet. The MBJ is a wire from the neutral bus to the cabinet enclosure.
The GEC enters on the other side of the cabinet, and terminates to the enclosure where it enters.
My argument is the GEC must terminate to the insulated neutral bus first, then let the MBJ bond the cabinet.
My contractor insists this meets the intent of 250.24(A)(4). I say it does not because the cabinet does not have a ground bus per say, only the cabinet enclosure.
What is your opinion?